I am looking at installation of a 750 HP, 575V motor on a VFD. The motor has a nameplate of 770 FLA, and the VFD supplier says that software will limit the VFD output to 770 A. I would like to use MC cable between the VFD and motor, and am looking at using one that is type MC-HL, even though it is not a hazardous location. I'm looking at two possible cable types, both are continuously welded corrugated aluminum sheath, with a rubber jacket. I would use (6) parallel cables, size 2/0.
I calculate the minimum ampacity required as 770x1.25 = 962.5 A. Using six parallel cables, I need 161 Amps per cable, and 2/0 is good for 175 A.
The problem is the equipment grounding. The cable I want to use has (3) #10 ground wires and (3) 2/0 conductors. I figure that the combination of the ground wires with the aluminum sheath is good as long as the ground fault protection is set at 200 Amps or less. This is some specialized equipment, and the equipment supplier has been trying to get information out of their VFD maker (in Europe) on the ground fault protection. They had assumed that the ground fault setting would be well under 200A, but had not been able to tell me an actual number.
Today, I saw a copy of the generic installation manual from this VFD maker. It contains the statement "Earth fault protection--In case of earth fault in motor or motor cable, only the inverter is protected". I am trying to get some clarification on this.
My other option is to get a similar cable, but with (4) 2/0 conductors and (1) #6 ground. I could use the 4th 2/0 as the new ground, which should be good for overcurrent protection up to 1000A. The color code in the cable is black-red-blue-orange plus green #6. Can I re-identify the 4th 2/0 wire with green tape, and cut off and not use the #6 ground?
I calculate the minimum ampacity required as 770x1.25 = 962.5 A. Using six parallel cables, I need 161 Amps per cable, and 2/0 is good for 175 A.
The problem is the equipment grounding. The cable I want to use has (3) #10 ground wires and (3) 2/0 conductors. I figure that the combination of the ground wires with the aluminum sheath is good as long as the ground fault protection is set at 200 Amps or less. This is some specialized equipment, and the equipment supplier has been trying to get information out of their VFD maker (in Europe) on the ground fault protection. They had assumed that the ground fault setting would be well under 200A, but had not been able to tell me an actual number.
Today, I saw a copy of the generic installation manual from this VFD maker. It contains the statement "Earth fault protection--In case of earth fault in motor or motor cable, only the inverter is protected". I am trying to get some clarification on this.
My other option is to get a similar cable, but with (4) 2/0 conductors and (1) #6 ground. I could use the 4th 2/0 as the new ground, which should be good for overcurrent protection up to 1000A. The color code in the cable is black-red-blue-orange plus green #6. Can I re-identify the 4th 2/0 wire with green tape, and cut off and not use the #6 ground?