Using a cable tray system with multiple PVC Coated MC Cable assemblies. All cable assemblies are copper. My question: There is a 3-phase 600amp load. Can you use a 3c-350 cable assembly in parallel? The ground conductor in the manufactured cable is only a #3 bare.
It is my understanding you cannot use this due to the ground size is not adequate. The ground has to full size, which would be a #1.
However if the cable tray is bonded properly could you use the tray as the equipment ground?