Article 250.112 requires that in parallel runs the grounds must be sized to the overcurrent protection. This I understand. But when it comes to motors I am finding confusion among engineers and inspectors on using this along with Article 430.52 Exception #1. In researching several engineered prints and talking to Engineers I have found they all use the size of the running load of the motor to determine the feeder size the calculate the ground based on the conduction size (example 400 amps parallel 250 KCM cu with a #2 ground.) then use Exception #1 to set the trip rating @ 500 amps. I am finding the the inspectors are running a 50-50 split on agreement and disagreement. What is the correct answer to this question?
Thanks
Pat
Thanks
Pat