Jeffreborn2007
Member
- Location
- Vacaville, CA, USA
I am developing a project that will require 8 parallel sets of 700 kcmil aluminum for a 1000A 480V 3PH-4W circuit. I will utilize a 500 kcmil copper ground for each set.
Per NEC article 215.2(A)(2) I believe I can run a 700 kcmil aluminum in only 1 of the sets as allowed per 250.122(F). Please advise.
Per NEC article 215.2(A)(2) I believe I can run a 700 kcmil aluminum in only 1 of the sets as allowed per 250.122(F). Please advise.