ceb58
Senior Member
- Location
- Raeford, NC
Looking at an install done on an inverter brought this question to mind. Here is the set up. Supply side taps from main panel to fused disconnect for inverter 2 hot 1 neutral. In the disconnect neutral has bonding screw installed and a new ground rod installed and grounding electrode conductor bonded to neutral bar and bonded back to the original GEC . From there it is 4 wire to inverter 2 hot 1 neut. 1 EGC. My thought is because the neutral in the main panel is already bonded to the original grounding electrode and now you have tapped that neutral there is no need for the GEC to rebond at the disconnect. The only bonding jumper should be from the original rod to the new second G rod. I am thinking this bond from the disconnect could become a parallel neutral or is it over thinking the thing?