Came across a situation today and was wonder what your thoughts were on this.
Aside from an absolute mess, what would you refer to this as: paralleled neutral, shared neutral, or something else entirely?
Note: This is confusing, even when looking at it.
2 12/2's leave a panel and each hit a time clock. From the time clocks, 2 more 12/2's (load side) leave the time clocks and enter a junction box. Inside the jbox, the 12/2's connect to two 12/3's in this manner: the neutrals are tied together and the black from the 12/2's are connected to the red on the 12-3's. Those two 12/3's come from the panel where the blacks are landed on breakers and the reds are spliced with 2 the red's from 4 other 12/3's (one red from the jbox 12/3's are spliced with two other red's in the panel.) The blacks from the other 4 12/3's are also landed on breakers. All the neutrals are tied in to the neutral bar at the panel. Back at the jbox, the black from the 12/'3's are tied with the blacks from two more 12/3's, the neutrals are tied with the neutrals from the two additional 12/3's, and the reds from those additional 12/3's are connected to the blacks of two more 12/2's coming from the panel, and all the neutrals are tied together. No two pole breakers were used, no handle ties were used, but this is a much older instal and it's a possibility that this was a multiwire branch circuit venture gone horribly awry. It looks like they just pulled neutrals from anywhere possible and ended up mixing and matching neutrals from as many as 4 circuits at one time.
Needless to say, I didn't want to be the last one to touch this. I told the customer that unless they wanted to pay me to completely rewire these circuits, I would not touch anything on them or add anything to them. Good call I think.
Any thoughts on what this mess would actually be called or referred to by the NEC would be greatly appreciated.
Thanks
Aside from an absolute mess, what would you refer to this as: paralleled neutral, shared neutral, or something else entirely?
Note: This is confusing, even when looking at it.
2 12/2's leave a panel and each hit a time clock. From the time clocks, 2 more 12/2's (load side) leave the time clocks and enter a junction box. Inside the jbox, the 12/2's connect to two 12/3's in this manner: the neutrals are tied together and the black from the 12/2's are connected to the red on the 12-3's. Those two 12/3's come from the panel where the blacks are landed on breakers and the reds are spliced with 2 the red's from 4 other 12/3's (one red from the jbox 12/3's are spliced with two other red's in the panel.) The blacks from the other 4 12/3's are also landed on breakers. All the neutrals are tied in to the neutral bar at the panel. Back at the jbox, the black from the 12/'3's are tied with the blacks from two more 12/3's, the neutrals are tied with the neutrals from the two additional 12/3's, and the reds from those additional 12/3's are connected to the blacks of two more 12/2's coming from the panel, and all the neutrals are tied together. No two pole breakers were used, no handle ties were used, but this is a much older instal and it's a possibility that this was a multiwire branch circuit venture gone horribly awry. It looks like they just pulled neutrals from anywhere possible and ended up mixing and matching neutrals from as many as 4 circuits at one time.
Needless to say, I didn't want to be the last one to touch this. I told the customer that unless they wanted to pay me to completely rewire these circuits, I would not touch anything on them or add anything to them. Good call I think.
Any thoughts on what this mess would actually be called or referred to by the NEC would be greatly appreciated.