jeremiahfpoa
New member
I would like to use two portable generators to feed the same buss - I don't think it's possible, but wanted to be sure. If it's not, I'm trying to understand why not.
Thanks
Thanks
If you set them up with synchronizers, load share modules, voltage regulators, etc ... like a regular paralleled generator project, then all is good. Generally with portables, that is difficult.
Here's a question that may help the OP (or not), but I'm asking the rest of you and not him. What if he fed each genset to a seperate leg of a subpanel? I'm guessing this would fall outside of the UL rating? Obviously there is the potential problem of installing a double-pole breaker which would have two out-of-phase legs.
Here's a question that may help the OP (or not), but I'm asking the rest of you and not him. What if he fed each genset to a seperate leg of a subpanel? I'm guessing this would.fall outside of the UL rating? Obviously there is the potential problem of installing a double-pole breaker which would have two out-of-phase legs.
Well you can if you want to .I would like to use two portable generators to feed the same buss - I don't think it's possible, but wanted to be sure. If it's not, I'm trying to understand why not.
Thanks
Well you can if you want to .I would like to use two portable generators to feed the same buss - I don't think it's possible, but wanted to be sure. If it's not, I'm trying to understand why not.
Thanks
Another concern is that when you put two generators in parallel, you essentially double the amount of fault current that can be supplied to the panel to which they are connected. Have you verified that that panel can handle the higher fault current.
Interesting that (no one says) its not against code or UL rating to supply one panel with two sources. I expected an immediate "no"!
I had presumed (bad thing to do) that the OP meant that there would be a synchronizing panel ahead of the one panel to get two sources. If you meant that you use one "main breaker" on a panel to connect one generator, and use a second "main breaker" on the same panel to connect the other generator, then the panel in question will have to have been designed for that configuration.Interesting that (no one says) its not against code or UL rating to supply one panel with two sources. I expected an immediate "no"!
Interesting that (no one says) its not against code or UL rating to supply one panel with two sources. I expected an immediate "no"!
I'm gonna use that one! It'll be great for management and nosy operators that won't understand your answers any way.dalesql said:automagically
What do you think the utility does nationwide. Multiple generators supplying the loads. Paralleling generators is a a VERY common practice.
Another concern is that when you put two generators in parallel, you essentially double the amount of fault current that can be supplied to the panel to which they are connected. Have you verified that that panel can handle the higher fault current.
Just in your mind. i'm currently working with a pair of 800kw, on trailers, self contained, even a fuel tank. You really need to get out of this Coleman/Briggs mindset.:grin:But theirs aren't portable ---
Never seen one, and I wouldn't think one ever would. For this application, one could assume the gen sets are not electronic feedback allowing positive rotor lock - rather it is likely they are in droop. They will load share fine, just not perfect. That means the power angle is not the same, so the rotors will not be in the same postion.--- No one's mentioned a sync. with mechanical linkage (belt/chain)? ---