kauf connect
Member
- Location
- Mooresville, Indiana, USA
I'm working with a customer who is putting cellular radios up a tower. For long runs from the power source, the AWG8 cable has too much voltage drop. It is -48v DC, 20A. The proposed solution is to run two cables (two conductor, shielded) up to tower. They will not increase the current, just hoping the extra copper gets enough power to the radio. Since the radio only has one bayonet mating, 2 pole power input, we designed a Tee adapter. This seems to be a violation of NEC 310.4, but we have no expert in this area. Our thought was this could be an exception, since a single cable can still handle the current if one of the two is disconnected. Larger conductor size in a single cable is not an option due to the size limits on the 2 pole connector (connector is UL 1977 / IEC 61984 approved). Hoping someone familiar with NEC or NFPA can provide some guidance. Thanks.