Re: Parallel Residential Service
I don?t think so. First of all, I don't see the word "underground" in paragraph 310.15(B)(6). Secondly, I think the code's authors constructed that Table with a specific configuration in mind. But they did not document their thought process in an FPN or in any other way that permits the reader to extend the logic into a different configuration.
For example, you would normally be limited to 175 amps (75C) for a 2/0 copper. If you double that by paralleling two 2/0 cables, you double the 175 to 350, not to 400. This is one of many cases I?ve seen recently in which I would not recommend doing anything that the Tables, Articles, or notes do not explicitly say is acceptable.