We need to feed an existing subpanel and increase its capacity from 60 to 100A. The feed comes through a 3/4" conduit, and there are spare conduits.
The code prohibits running parallel cables smaller than 1/0". I'm not entirely convinced by the reasons, but that's the rule.
We're trying to find a solution before running new conduits and wires.
There could be another solution if we find a third conduit coming out of the same panel based on 300.3(B)(1):
Exception: Conductors installed in nonmetallic raceways run underground shall be permitted to be arranged as isolated phase, neutral, and ground conductor installations. The raceway shall be installed in close proximity, and the isolated phase, neutral, and grounded conductor shall comply with 300.20(B).
I understand this means we can run:
Has anyone done something like this, and is there anything that would prevent me from doing it? I've seen installations like this for large service wires, but never for small ones.
The code prohibits running parallel cables smaller than 1/0". I'm not entirely convinced by the reasons, but that's the rule.
We're trying to find a solution before running new conduits and wires.
There could be another solution if we find a third conduit coming out of the same panel based on 300.3(B)(1):
Exception: Conductors installed in nonmetallic raceways run underground shall be permitted to be arranged as isolated phase, neutral, and ground conductor installations. The raceway shall be installed in close proximity, and the isolated phase, neutral, and grounded conductor shall comply with 300.20(B).
I understand this means we can run:
- phase A, in one conduit. Wire #3 AWG.
- phase B, in another conduit. Wire #3 AWG.
- Neutral and ground in the 3rd separated conduit, maybe.
Has anyone done something like this, and is there anything that would prevent me from doing it? I've seen installations like this for large service wires, but never for small ones.