Parallel runs with grounding conductor

Status
Not open for further replies.

Jsybrandy

Member
Location
OH, USA
I have a system that utilizes multiple power feed tap points - i.e. the power feed is running parallel from one fixed point to different tap points. Normally, I would run the grounding conductor with these ungrounded feeds, but I am wondering if there are any exceptions to this rule (reference 250.25(C) ). Or does the NEC mandate that this is the case at all times?

Thanks,
 
250.25(C) addresses the grounded conductor and, other than being required at a grounded service, bringing that conductor to downstream panels/equipment is optional. Your post mentioned grounding conductor which would be required in most, if not all, conditions although it can be a qualified raceway and not an actual conductor.
 
fair enough, I agree. However, my question is more based on whether the grounded conductor must be ran parallel to the ungrounded conductor(s) or can it take a different path?
 
fair enough, I agree. However, my question is more based on whether the grounded conductor must be ran parallel to the ungrounded conductor(s) or can it take a different path?
It appears to confirm then, that there really is no exception and the EGC needs to be parallel with the ungrounded conductors.
You're confusing us:
grounded = neutral
grounding = EGC
 
of course you are right, sorry for confusing - let's stick with grounding (EGC)

The only exceptions to running the grounding conductor (EGC) with the rest of the circuit conductors (in same raceway or in same cable) is when adding a grounding conductor to an existing circuit (such as a residential receptacle circuit) when there is no raceway in which to pull an additional conductor.
 