misterbill1972
Member
- Location
- Cali
I have a 1200A 3PH 480V existing parallel circuit with the wrong size wire. I am running an additinal 3" conduit and I will be pulling (3) 750 kcmil in each. My secondary goes to a box on the motor. this has (2) pre-threaded 5" holes. I will reduce these down to 4". My questian is I cannot fit (9) 750 kcmil in (2) 4" conduits. I can fit (12) 700 kcmil. I have already done the derating and correction factors. It will work. Is this in any way a NEC violation. I cannot find anything to say it is, but still wonder. Any comments will be appreciated.