This isn't your typical parallel / series question. Engineers before me designed our heating element boxes a certain way, and I'm not sure why they did it.
Its a bank of heating elements run off of 480VAC / 1 Phase power. It was designed with 240VAC 1625W elements, run in a parallel/series configuration (bottom configuration on the attached image). This unit is advertised as 19.5kW, but I'm getting half of that if I'm looking at it correctly. I want to run 480VAC 1625W heating elements in a parallel configuration (top on attached image).
Any thoughts or ideas on why it was configured as it was? Am I missing something?
(Notes on drawings: there are 12 heating elements in each box, #1 on the top is the same element as #1 on the bottom. The elements contained within a box are connected via a busbar. A1 and B1 are from a single contactor, A2 and B2 are a separate contactor. This allows us to run this unit at half power.)
Its a bank of heating elements run off of 480VAC / 1 Phase power. It was designed with 240VAC 1625W elements, run in a parallel/series configuration (bottom configuration on the attached image). This unit is advertised as 19.5kW, but I'm getting half of that if I'm looking at it correctly. I want to run 480VAC 1625W heating elements in a parallel configuration (top on attached image).
Any thoughts or ideas on why it was configured as it was? Am I missing something?
(Notes on drawings: there are 12 heating elements in each box, #1 on the top is the same element as #1 on the bottom. The elements contained within a box are connected via a busbar. A1 and B1 are from a single contactor, A2 and B2 are a separate contactor. This allows us to run this unit at half power.)