parallel service feeders

Status
Not open for further replies.
I have a situation where i have an existing 100 service to a warehouse, with the proper sized conductor and conduit for the use. The customer wants to get more power to his unit (200 amps), my thought was to run a new parallel set along the existing one, which would be cheaper than tearing down and replacing with a larger conduit and conductors. My issue is the area around where the new service disconnect will be installed may only allow me to run one conduit out. Can I run a 4/O (Alum) out to a large junction box, just outside the meter room, and tap into a parallel set from that point? Of course keeping everything equal. I do this all the time on the load side of service disconnects in troughs, but can't think of a time I tapped anything on the load side.
 
Keep in mind conductors are not generally paralleled unless they are a min. size of 1/0
What size conductor to the original 100 amp

what size service does this ware house have. it sounds like there are multiple tenant units
 
David, the main service size is not a problem, another tenant has isolated himself from the rest of the service, leaving room for the expansion. The conduit used for the existing service is 1 1/2" EMT so I have room to increase the wire size in that one.
Looking at the costs it may not be worth it in the long run.
 