parallel single phase

Status
Not open for further replies.

sgroats

New member
We have installed a new 400 amp single phase service to a small water pumping station. From the service we have 2-200 amp fused disconnects protected by 175amp breakers. From the load side of the disconnects we are feeding 2 variable speed drives, the problem is I cannot fit the 2/0 wire into the drive input terminals to my satisfaction. I want to run 2 conductors in parallel to each input. Question is #1 or #2 awg.
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
Re: parallel single phase

You can't parallel conductors smaller than 1/0 per 310.4.

If the breaker is 175 amps, and only feeds a motor, you could probably reduce the wire to a single #1 or #2 depending on the size of the motor.

For a motor, the wire doesn't have to have the same ampactiy as the breaker.

Steve

[ July 20, 2005, 09:17 AM: Message edited by: steve66 ]
 

milwaukeesteve

Senior Member
Location
Milwaukee, WI
Re: parallel single phase

I concur with Steve.
Check 430 and the nameplate to see what size conductor you truly need. It may be that you only need #1 or #2. That may help.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: parallel single phase

There are a couple of problems I see.

1)As has been stated you can not parallel conductors smaller than 1/0.

2)VFDs, these throw a major wrench in your plans. The feeder to a VFD must be sized based on the input current marked on the VFD regardless of the motor size. 430.2

Use a 25 HP VFD for a 5 HP motor and you still feed the VFD like it was running a 25 HP motor.
 