pwest
Member
- Location
- Roxbury, CT
I have a question regarding taps of parallel feeders.I am working in a shopping center with an existing 800Amp service. There are 2 sets of 500MCM in a trough fed from an 800Amp Main Breaker (They are joined together at both ends,same length, same insulation etc. in compliance with article 310-4).There are multiple taps to multiple disconnects, in compliance with article 240-21(taps not over 10ft long). The taps are connected to 1 set of 500MCM. The local inspector states that the tap must be connected to BOTH sets of 500MCM.In other words a connection with (2)500mcm run and (1)#2 tap. He states that the 1 set of 500MCM is only rated for 400Amps with over current protection at 800Amps and the connection of the 2 sets of 500mcm at the end of the trough is insignificant. Is this so???? If so, where does it appear in the NEC