Well, I kinda got thrown into a project started by someone else.
PV system with panels and inverters on a building with POCO single phase service on another
about 100 ft. between buildings with about 150 ft. total length of wire
Having a problem with overvoltage on inverters when sun is at peak.
Wires were already replaced with larger(2/0 AL.)
peak output on wires is about 86 amps.
according to calc (
http://america.sma.de/vdropcalculator.html) voltage rise is still not quite at recommended level
When looking at job, thought crossed my mind about paralleling wire between buildings, which is what prompted question because I had never seen it done before.
POCO will not change transformer because it is within specs.
Humor me here-- Wire (3-insulated and 1-uninsulated) between buildings has the bare wire and one of the insulated wires joined together at both ends.
So I have 2 hots and a paralleled neutral, I was thinking of seperating the insulated neutral from bare and paralleling it with one of the hot legs to see what effect that has on the voltage rise of that leg compared to the other one.
Worth the effort or not??