I have some concerns about code permissibility and questions on how this should actually be executed.
Need a 3000A @480V service. Utility has (2) 1250kVA pad mount transformers, which would be 1500A each, that they said they are willing to parallel them in order to get our 3000A service capacity. The secondaries of both would terminate on a single 3000A CB that would service as the service disconnect.
Trying to navigate 230.2 and other sections for what applies. I don't think this counts as two services. But also, if utility isn't connecting their secondaries together at source side, this isn't a truly parallel feed. I'd be concerned about not knowing if one of sets of conductors to one of the transformers is overloaded. The main CB wouldn't see this as overload scenario.
I suspect the secondaries will have to get connected together at source side, but is that 100% true for requirement? Anything else I'm missing?
Need a 3000A @480V service. Utility has (2) 1250kVA pad mount transformers, which would be 1500A each, that they said they are willing to parallel them in order to get our 3000A service capacity. The secondaries of both would terminate on a single 3000A CB that would service as the service disconnect.
Trying to navigate 230.2 and other sections for what applies. I don't think this counts as two services. But also, if utility isn't connecting their secondaries together at source side, this isn't a truly parallel feed. I'd be concerned about not knowing if one of sets of conductors to one of the transformers is overloaded. The main CB wouldn't see this as overload scenario.