I need a sanity check, when paralleling wire there will be times when I need a full size EGC, correct?
Each EGC needs to be sized as if it was the only one.I need a sanity check, when paralleling wire there will be times when I need a full size EGC, correct?
250.122(F) sized per OCPD
Suspected such. If I decide to do a 4000 amp feeder in 4/0 sets, I can get away with a 4/0 EGC, correct?
No...full sized in each raceway based on the 4000 amp OCPD. CMP 5 is on record saying that the size of the circuit conductors for a parallel system is the sum of all of the conductors connected in parallel and it is not the size of the ungrounded conductors in each raceway.Suspected such. If I decide to do a 4000 amp feeder in 4/0 sets, I can get away with a 4/0 EGC, correct?
No...full sized in each raceway based on the 4000 amp OCPD. CMP 5 is on record saying that the size of the circuit conductors for a parallel system is the sum of all of the conductors connected in parallel and it is not the size of the ungrounded conductors in each raceway.
You need a 500 kcmil EGC in each raceway for that system, no matter what size the ungrounded conductors are in each raceway.
CMP 5 is on record saying that the size of the circuit conductors for a parallel system is the sum of all of the conductors connected in parallel and it is not the size of the ungrounded conductors in each raceway.
The size of the ungrounded conductors in this case would be the the size of all of one set of parallel conductors. 18 x whatever kcmil size 4/0 is.Code says you do not need a larger EGC then the ungrounded conductors.
The size of the ungrounded conductors in this case would be the the size of all of one set of parallel conductors. 18 x whatever kcmil size 4/0 is.
Let's say I want to use 3 sets of 600 kcmil copper for a 1200 amp feeder. The size of the ungrounded conductor is 1800 kcmil.
No...full sized in each raceway based on the 4000 amp OCPD. CMP 5 is on record saying that the size of the circuit conductors for a parallel system is the sum of all of the conductors connected in parallel and it is not the size of the ungrounded conductors in each raceway.
Code says you do not need a larger EGC then the ungrounded conductors.
CMP 5 says that for a parallel circuit the size of the ungrounded conductor is the sum of the areas of the conductors connected in parallel.Can you elaborate more on this or link to it? I'm a bit confused by this statement. I'm reading it to take the EGC as part of that sum... however I can't see the EGC being larger than the current carrying conductors in any given conduit.