400amp/480VAC Feed to a MCC from a Panelboard.
Conduit Run is approx. 200FT.
I would like to run 2-4/0's per phase and 1-#3 gnd in a 4"Conduit. This is because we have a lot of it in stock.
Since there would be six 4/0's in the same conduit (Six current carrying conductors)then Table 310-15(b)(2)(a) applies with 80% derate.
So in order to stay with 2-4/0's per phase, the wire would have to be 90degC rated according to Table 310-16.
1-4/0 = 260amps
2-4/0's = 520amps
520x0.8=416amps
okay to use on 400amp breaker.
Just want to make sure I am thinking correct??
Conduit Run is approx. 200FT.
I would like to run 2-4/0's per phase and 1-#3 gnd in a 4"Conduit. This is because we have a lot of it in stock.
Since there would be six 4/0's in the same conduit (Six current carrying conductors)then Table 310-15(b)(2)(a) applies with 80% derate.
So in order to stay with 2-4/0's per phase, the wire would have to be 90degC rated according to Table 310-16.
1-4/0 = 260amps
2-4/0's = 520amps
520x0.8=416amps
okay to use on 400amp breaker.
Just want to make sure I am thinking correct??
