I am installing a 1200 amp 120/240 volt single phase service to supply a campground. What are the calculations to figure what I need for the paralleled conductors?
 
Re: Paralleled Conductors

Originally posted by drickert:
I am installing a 1200 amp 120/240 volt single phase service to supply a campground. What are the calculations to figure what I need for the paralleled conductors?
How many sets do you want to run?

Do you plan on keeping them in separate raceways?

For a full 1,200 amps 3 sets of 600 kcmil copper or 4 sets of 500 kcmil aluminum in separate raceways will do it.

[ December 06, 2005, 07:59 PM: Message edited by: iwire ]
 
Re: Paralleled Conductors

Are there any significant distances involved, such that voltage drop becomes a possible issue?
 
Re: Paralleled Conductors

Originally posted by drickert:
I am installing a 1200 amp 120/240 volt single phase service to supply a campground. What are the calculations to figure what I need for the paralleled conductors?
I don't know what you have in mind. How about you show us your calculations and we'll look at them and let you know if you are on the right track!
BTW T310.16, 310.4 Chapter 9 Annex C couple places to start
 
Re: Paralleled Conductors

I got a PM from drickert explaining his situation more.

He really wanted to find a way to 'fit' 1,200 amps of aluminum conductor in two 4" raceways.

My response was that it was not possible and offered a suggestion of doubling the voltage to get the equivalent KW through the raceways.

If anyone has some more suggestions please add them, maybe I am missing something.

Bob
 
Re: Paralleled Conductors

Bob,
I think it can be done using compact strand conductors. Twelve compact strand 250kcmil will fit in 4" rigid. That would let you have 4 sets of 3 conductors in each raceway. The grounded conductor is not current carrying so we have 8 current carrying conductors and a derating of 70%. 250kcmil aluminum is 230 amps at 90C leaving 161 amps after derating. That would give you 644 amps per raceway. Note that if the raceway in not metallic, this solution won't work as EGCs would be required and they won't fit.
Don
 
Re: Paralleled Conductors

Pretty neat Don.

I do not know the raceway type (or length).

I believe he was talking service entrance conductors so the EGC may unneeded.
 