tower
Member
- Location
- Massachusetts
say you have a continuous feeder loaded of 724 amps and the conductors are paralleled 4 times per phase to 75 degree terminals. after the calculations you come up with the phase conductors being sized at 4/0 awg. with out going into calculations, my question is. how is it that the amperage is assumed to be evenly divided amongst the paralleled conductors.say 230 amps per phase for a total of 920 amps.is there a capacity at which each 4/0 will realize.can one phase over heat.our is it like working with 4 electricians roughing in a office space.you no every body doesnt pull there fair share one way or another,and the poor bastard that is`nt freinds with the project manager is giong to have to carry the lazy fat slub if he wants to keep his job.its relative is`nt it? or is there a mathamatical engenering answer ?