chuck@apsinc.biz
Member
- Location
- Colorado
A particular UPS manufacturer calls for parallel runs to feed and distribuite power with-in the UPS system, then doesn't provide the necessary conduit entry space for separte conduits for each set of parallel feeders. A solution presented is to install 1 oversized raceway for each feed and put the paralleled feeders in the same raceway. Provided the derating provisions of NEC 310 are followed, I do not see any code issues with this solution. Does anyone have any information that contradicts this? Is my power quality compromised in any way?