In a paralleled motor feeder application would there be any adverse issues to connect 1 of the Paralleled L1 feeder wires to T6 and the other Paralleled L1 wire to T1? Typical for the remaining connections for L2 & L3.
This is an 300 HP inverter duty rated 480 Volt, 3 Phase Motor connected for typical Across-the-line Delta Run, L1 to T1-T6, L2 to T2-T4, L3 to T3-T5. The motor is started using a VFD with a load side reactor in which the motor is overrun to 65Hz. The VFD is released at the overrun speed and the motor is then connected across the line with an magnetic motor starter contactor.
The new motor has parallel wring for each motor winding connections. Example: 2 wires for T6, 2 wires for T1, etc., 12 Total wires for motor. Not a 12 lead motor. If connected normally the L1 motor connection would have 2-250 Parallel wires, 2-Parallel Motor wires for T6, and 2-Parallel Motor wires for T1 for a total of 6 wires in each motor connection. This becomes a bulky connection. I have an electric hydraulic crimp tool and my preference is to use crimp lugs with grade 8 bolts for a positive and secure electrical connection. The connection would be insulated with 600 volt rated cold or heat activated heat shrink tube insulation.
My thoughts are that this should not be an issue because:
This is an 300 HP inverter duty rated 480 Volt, 3 Phase Motor connected for typical Across-the-line Delta Run, L1 to T1-T6, L2 to T2-T4, L3 to T3-T5. The motor is started using a VFD with a load side reactor in which the motor is overrun to 65Hz. The VFD is released at the overrun speed and the motor is then connected across the line with an magnetic motor starter contactor.
The new motor has parallel wring for each motor winding connections. Example: 2 wires for T6, 2 wires for T1, etc., 12 Total wires for motor. Not a 12 lead motor. If connected normally the L1 motor connection would have 2-250 Parallel wires, 2-Parallel Motor wires for T6, and 2-Parallel Motor wires for T1 for a total of 6 wires in each motor connection. This becomes a bulky connection. I have an electric hydraulic crimp tool and my preference is to use crimp lugs with grade 8 bolts for a positive and secure electrical connection. The connection would be insulated with 600 volt rated cold or heat activated heat shrink tube insulation.
My thoughts are that this should not be an issue because:
- Each winding connection of T6 & T1 are receiving the same phase.
- The motor feeder wires of L1 are joined in the reactor thereby connecting T6 & T1 together bridging the motor windings. Additionally, the motor feeder wires of L1 are joined at the motor contactor.
- If this was a Wye Start Delta Run application, the motor winding connections would be installed individually and joined together at the motor control center starter.