Pressure
Member
- Location
- Lawrence, KS
- Occupation
- Design Engineer
I am designing a system, that will require (2) AC PV Inverter Output Combiners. Each combiner will be rated at 800A with a 800A Main OCPD, and have 752A at the continuous use rating. I would like to then parallel the output of each combiner to a single 1600A Fused AC PV Disconnect. Each Combiner will require (3) Sets of [(3) 400kCMIL AL and (1) #1/0 AWG EGC CU in 2.5" Conduit to the 1600A AC PV Disco.
The question is in regard to the paralleling of the (2) power sources and their distances from each other. I am calculating a 2.02V drop @ 0.42% for the first combiner, and a 5.79V drop @ 1.21% for the second combiner. I do not believe this violates any paralleled conductor rules, but I could be wrong. Can I potentially increase the conductor size of the second combiner to bring it closer to the Vdrop of combiner 1, or do I need to have both combiners next to each other and have the same size and length of conductors for each?
Any insight into best practices for this situation would be appreciated. Thanks.
The question is in regard to the paralleling of the (2) power sources and their distances from each other. I am calculating a 2.02V drop @ 0.42% for the first combiner, and a 5.79V drop @ 1.21% for the second combiner. I do not believe this violates any paralleled conductor rules, but I could be wrong. Can I potentially increase the conductor size of the second combiner to bring it closer to the Vdrop of combiner 1, or do I need to have both combiners next to each other and have the same size and length of conductors for each?
Any insight into best practices for this situation would be appreciated. Thanks.