Came across an unfinished project from another contractor that I was asked to check over. I was not asked to inspect, but to determin what was needed to finish the project. From a new generator with a 400amp main 2 parallel runs of #4/0 were run inside the building. 800 ft (estimated) away the runs were installed in a junction box and terminated together. From the termination 2 #6 wires were run to different 60amp fused disconnects. After telling the building owner of this installation I was asked to identify what was against code. The #6 on a 400amp breaker is easy. Can parallel runs terminate in a junction box and then feed different equipment? I can't find it in the book. I always practiced that parallel runs had to start and end at a device such as a breaker or disconnect.
Chris
Chris