I was called to do an EMF survey of a house where an average of about 2.5 amps of neutral was running through the grounding electrode conductor to the water service pipe. The conductor path took it under a child's bedroom where a four-hour data logging showed a magnetic field average of 4.6 Mg. This was a concern since the WHO has verified that large studies show a doubling of childhood lekemia at 4 mG and above. A current of 5 amps produces a magnetic field of 10 mG at one meter from the conductor.
This is just an introduction to my real question: there are two main panels in the basement. They are bonded by a conductor between their grounding busses. The neutral and grounding busses are bonded in both panels. Thus the neutral current is paralleled back to the meter box. So it seems that the hots are not paralleled but the neutrals are. Any comments? The maximum net currents on the two service cables measured between a 19 amps and 15 amps.
One GEC from one panel goes to the ground rod outside, and the GEC from the other panel goes to ther water pipe clamp.
Karl
This is just an introduction to my real question: there are two main panels in the basement. They are bonded by a conductor between their grounding busses. The neutral and grounding busses are bonded in both panels. Thus the neutral current is paralleled back to the meter box. So it seems that the hots are not paralleled but the neutrals are. Any comments? The maximum net currents on the two service cables measured between a 19 amps and 15 amps.