DLCOX
Member
- Location
- Phoenix, AZ
Would this be considered paralleling breakers? Where 3 - 100A single bkr was used vs a single 3 ph 225A brkr. The goal is to put a 65kW load on the UDP.
I'm not an expert but this just seems off.
Ref: 208Y/120
View attachment 16630 vs View attachment 16634
Thoughts??
Thanks
Idea was to use a breaker that could give us 65kW (80% of 81kW) load at 208V. A 225A Bkr would do the trick. The whole reason for using 100A bkrs was because of supply. There are no 225A bkrs laying around therefore would be costly to purchase them since we need enough bkrs to connect 64 Load Banks.
As far as the Load Bank connectors, they do represent a single 3 phase setup.
View attachment 16638
Idea was to use a breaker that could give us 65kW (80% of 81kW) load at 208V. A 225A Bkr would do the trick. The whole reason for using 100A bkrs was because of supply. There are no 225A bkrs laying around therefore would be costly to purchase them since we need enough bkrs to connect 64 Load Banks.
As far as the Load Bank connectors, they do represent a single 3 phase setup.
View attachment 16638
JF,
Upstream to this are 9 2MW UPSs fed from some MSBs. The room is a Data Center Vault. So eventually the entire vault would need to be tested to its max capacity. Attached is a picture of the upstream Power Distribution to give a clearer picture.
When you commission these types its generally done at 80% which is a common mark in the electrical world.
I was presented with what I showed you all and I didnt think it was the best way to go so again I enlisted you all feedback to get some thoughts on the matter.
View attachment 16640
J...
...I was presented with what I showed you all and I didnt think it was the best way to go so again I enlisted you all feedback to get some thoughts on the matter.
Two line side terminals are connected to same point somewhere upstream, two load side terminals are connected to same point somewhere downstream, if subjected to ideal conditions each breaker carries half the load, such ideal conditions are difficult to achieve and is why it is not ordinarily allowed for NEC applications. If part of a listed assembly - the listing and testing of it determined it is suitable.Kwired,
Let me ask this question then.
What exactly is paralleling Breakers.
DC