My buddy calls and is talking about his new pool. Pool guy will let him provide the service to the pool. It is 155' from his service entrance and only 40 amps is required. He owns a six conductor, 6AWG cu. SO/SOOW cable that he wants to use. So far I don't have a problem but considering VD, would paralleling the 240 and neutral and adding a separate EGC be a terrible idea? Conductors are smaller than 1/0 but not being paralleled for ampacity. I am thinking about what will fit where? Neutral buss won't be a problem but the hot pairs might need to be turned into a single conductor to fit in the chosen breaker. I imagine this cable will be buried in a plastic conduit. So now I am thinking about derating the single conductors. I have not looked at one NEC table before I started this thread. I am almost willing to provide what he needs and trade for that cable just to have on hand.
Paralleling conductors discussed in an earlier thread;
http://forums.mikeholt.com/showthread.php?t=175353&highlight=Paralleling+cond uctors
Paralleling conductors discussed in an earlier thread;
http://forums.mikeholt.com/showthread.php?t=175353&highlight=Paralleling+cond uctors