If it is smaller than 1/0AWG the NEC will prohibit paralleling at all.?View attachment 14602 please see attached pic. I need to parallel 2 conductors of a multi-conductor cable to keep voltage drop within acceptable range.
my question is... I know I need to parallel the line conductors for this to work but do I also need to parallel the neutral conductors as well?
thank you
He's only paralleling for voltage drop, not ampacity as I understand it.In that application, a series circuit, the neutral would carry the same amount of current as the line conductors, so yeah the neutral would need to be paralleled/sized the same as the line conductors.
He's only paralleling for voltage drop, not ampacity as I understand it.
I don't see any problem with paralleling two ungrounded conductors (1/0 or larger) and not the neutral.
What's to explain? Assume one ungrounded and one neutral complies with ampacity requirements. Parallel one side of the circuit increases ampacity on that side, but does not reduce ampacity on the other.Must resist urge to ask to explain.
Must resist urge to ask to explain.
Must resist urge to ask to explain.
Urge not resisted.
Explain please.
You can decrease voltage drop by just increasing the size or quantity of conductors used for one side of a two wire circuit.
As long as the smaller conductors are rated for the application the NEC does not prohibit it is.
Plus there is the fun of providing a What the heck? moment for the next guy that goes to service it.
What's to explain? Assume one ungrounded and one neutral complies with ampacity requirements. Parallel one side of the circuit increases ampacity on that side, but does not reduce ampacity on the other.
He's only paralleling for voltage drop, not ampacity as I understand it.
I don't see any problem with paralleling two ungrounded conductors (1/0 or larger) and not the neutral.
View attachment 14602 please see attached pic. I need to parallel 2 conductors of a multi-conductor cable to keep voltage drop within acceptable range.
my question is... I know I need to parallel the line conductors for this to work but do I also need to parallel the neutral conductors as well?
thank you
Conductors are #10 though not 1/0 or larger.
In that case, you are not allowed to parallel at all. Reference 310.10(H)(2).Conductors are #10 though not 1/0 or larger.
That is correct. Ampacity is no issue here at all. Just voltage drop. Conductors are #10 though not 1/0 or larger.
I got thrown off because I know in voltage drop calculations, total circuit length resistance is calculated.
I guess if I don't parallel the neutral, I cannot take credit for the decreased resistance for that portion of the circuit?
I assume that increasing the voltage was already considered and ruled out?
Code does not require parallel neutrals when you parallel line conductors. However there are potentially lots of detail devils in this sort of installation.
1) For the same total amount of copper, you get better reduction in voltage drop if that copper is evenly distributed. For a single phase circuit, half of the voltage drop is in each side, half on the 'line' and half on the 'neutral'.
If you double the 'line' conductors, then the _total_ voltage drop goes to 75% of the original value, because you still have the original voltage drop of the neutral.
2) As others have mentioned, code has a minimum size requirement for paralleling conductors.
3) When you parallel conductors, they must have the same 'characteristics'. In a multi-conductor cable you may need to consider symmetry and conductor lay to determine which conductors may be placed in parallel.
-Jon
If you look at what happens when there is a ground fault, you will see that the size of the grounded conductor is not important.Does the code require that you have symmetry in your conductor sizing for voltage drop curtailment in general?
Take a 40A line-to-neutral single phase load with a default size of #8 wire. Suppose you can either curtail voltage drop with a #6 wire for both line and neutral (what most people would do), or you can curtail voltage drop with a #2 line and keeping the #8 neutral as the default size. Why you would do the latter, I do not know. But that is the kind of solution that the OP is proposing, except involving parallel sets instead of a general upsizing.
This does seem like it opens a loophole in the requirement to proportionally upsize the EGC. Because it only requires this when you increase the size of the ungrounded conductors. If you only increase the size of the neutral to curtail voltage drop, and keep the line conductor equal to the minimum local size, then technically you haven't upsized the ungrounded conductors. It feels wrong, but like I said, it is a loophole.
Does the code require that you have symmetry in your conductor sizing for voltage drop curtailment in general?
It doesn't matter why you are paralleling the conductors, in general the code does not permit parallel conductors smaller than 1/0.That is correct. Ampacity is no issue here at all. Just voltage drop. Conductors are #10 though not 1/0 or larger.
I got thrown off because I know in voltage drop calculations, total circuit length resistance is calculated.
I guess if I don't parallel the neutral, I cannot take credit for the decreased resistance for that portion of the circuit?