Hoping someone can help.
Existing conditions:
2000 ft ductbank
old feeder 4-500 kcmil in one duct
not so old feeder 4-500 kcmil in another duct
cable insulation type of feeders may not match
existing load has been demolished
New load is 150kVA, 480V, 3PH
I would like to parallel the two sets of existing feeders in order to reduce the voltage drop from about 5% (if one set were used) to about 2.5% (using both sets). Since the ampacity of one set of cables is not a limiting factor, I don't see why 310.10(H)(2)(4) would apply. Would paralleling the two feeders with different insulation types violate the code in this case? If so, why?
Thanks in advance.
Existing conditions:
2000 ft ductbank
old feeder 4-500 kcmil in one duct
not so old feeder 4-500 kcmil in another duct
cable insulation type of feeders may not match
existing load has been demolished
New load is 150kVA, 480V, 3PH
I would like to parallel the two sets of existing feeders in order to reduce the voltage drop from about 5% (if one set were used) to about 2.5% (using both sets). Since the ampacity of one set of cables is not a limiting factor, I don't see why 310.10(H)(2)(4) would apply. Would paralleling the two feeders with different insulation types violate the code in this case? If so, why?