im designing a parallel genset system and while researching some criterions for it, i came across this article:
http://www.csemag.com/article/17522...eling_Generators_in_Critical_Applications.php
notice the one line, there is 6 generators in parallel. The gen ratings are 1800kW at 12470V, but the genbreakers are 1200A. It should be only maximum handle rating of (2250k/(12470*1.73))*1.25 or did i miss anything.
I am designing a parallel genset system rated at 2000kW each at 480. That gives me about 3000A handle rating on the paralleling gear with a 6000A bus. Its a 2 turbine hydro, so both generators are running all the time. Is there a swgr who can make such a big gear? or bigger? if we add a 3rd turbine?
the other thought is asking for a gen output at 5kV class....but the 480V gen output is a stock design.
http://www.csemag.com/article/17522...eling_Generators_in_Critical_Applications.php
notice the one line, there is 6 generators in parallel. The gen ratings are 1800kW at 12470V, but the genbreakers are 1200A. It should be only maximum handle rating of (2250k/(12470*1.73))*1.25 or did i miss anything.
I am designing a parallel genset system rated at 2000kW each at 480. That gives me about 3000A handle rating on the paralleling gear with a 6000A bus. Its a 2 turbine hydro, so both generators are running all the time. Is there a swgr who can make such a big gear? or bigger? if we add a 3rd turbine?
the other thought is asking for a gen output at 5kV class....but the 480V gen output is a stock design.