I have an installation where the 400 HP motors are fed using Type TC VFD Power Cables.
These particular cables incorporate (3) grounding conductors and appear to meet the requirements of 250.122(A) as "Sectioned" conductors but those "sectioned" conductors are sized per the one cable and not parallel cables in regard to the OCP ahead of the drives.
Would this be a violation as far as 250.122 sizing or is would the drive have a bearing on sizing the equipment ground ?
These particular cables incorporate (3) grounding conductors and appear to meet the requirements of 250.122(A) as "Sectioned" conductors but those "sectioned" conductors are sized per the one cable and not parallel cables in regard to the OCP ahead of the drives.
Would this be a violation as far as 250.122 sizing or is would the drive have a bearing on sizing the equipment ground ?