Parking Lot lighting requirements

Status
Not open for further replies.

bbenigni

Member
Location
Miami, Fl, USA
Hello all,

I am working on an R-3 residential building that includes a small 6 car parking lot.

Unfortunately parking lot lighting is not something i know very much about.

What codes govern the lighting of parking lots, when they are required and the illumination levels.

I am hoping to be able to get by without adding light poles, and just adding illumination from the building's second floor.

Thanks.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
The IESNA has recommended standards for parking lot lighting.
If you put lighting on the second floor, there will be a lot of glare and uplight. Luminare poles will do a better job.
Get together with you wholesale house and see if they can help you with a lighting layout

And drive around at night, look for applications similar to yours, to get an idea of how it will work.
And at lease stub out a couple of 1" conduits...
 
Generally there no parking lot lighting requirements in the widely used national codes - but check your local codes. Some cities limit lot lighting to prevent light pollution / light trespass, and others require minimum lot lighting for safety or security reasons.
 

ken44

Senior Member
Location
Austin, TX
Official guidelines by IES for foot candle levels on parking lots.

“Minimum horizontal point at any point should be .5fc and min vertical luminance at 5’ above finished grade is .25fc”.
 
Official guidelines by IES for foot candle levels on parking lots.

“Minimum horizontal point at any point should be .5fc and min vertical luminance at 5’ above finished grade is .25fc”.

Your information is a bit out of date. Older versions of the IES Handbook gave specific values like you state here, but they have backed off that kind of approach. The reason is that the lighting design industry now recognizes that the "correct" light levels for exterior environments vary widely depending on adjacent light levels, occupant activities, and occupant age. In other words, 0.5 fc / 0.25 fc minimums may provide good visibility in some scenarios, but not in all scenarios. Uniformity of illuminance is also an important consideration, because contrast has a huge impact on nighttime visibility.

(Reference - See Table 26.2 in the current Handbook (10th Edition). It does not give one-size-fits-all illuminance targets like previous editions did.)

Back to the OP's situation - most likely you are not code-required to light the parking lot at all. But if the owner wants to light it, you should consult someone with exterior lighting design knowledge. Manufacturers and suppliers will help for free.
 

raberding

Senior Member
Location
Dayton, OH
Occupation
Consulting Engineer
lot lighting

lot lighting

And pay attention to the local Zoning Regs. Some localities get very strict wrt Pole Ht, Color Temp, trespass, uplight pollution, BUG ratings, etc.
 

Ragin Cajun

Senior Member
Location
Upstate S.C.
Get with the local electric utility and have them do it. They do this every day and have the equipment to install and provide upkeep. And you don't have to provide power, they will.

RC
 

Howard.MF

Member
Location
US
The major requirement include brightness and lighting uniformity.

Depending on the preference of the owner, the brightness can be around 150 to 250 lux, and the lighting uniformity can be 0.6, which is the enough for residential use.
 

tw1156

Senior Member
Location
Texas
The major requirement include brightness and lighting uniformity.

Depending on the preference of the owner, the brightness can be around 150 to 250 lux, and the lighting uniformity can be 0.6, which is the enough for residential use.

This isn't making much sense in regards to lighting. Do you mean illuminance to be around 150 (~1.5fc) - 250lux(2.5fc) for the parking lot lighting with a uniformity ratio (max:min, avg:min?) of 0.6:1?

If not explicitly stated, I would typically design to a 0.5fc min (previously IES enhanced security lighting levels) with a max/min ratio of 15:1. With LED the uniformity is much easier to achieve versus the old HID days.
 
Status
Not open for further replies.