Ok so if you have a tube form set to a depth of 3' with a rebar cage inside, how do you get in and out of it with PVC that is at a 24" depth?
PVC goes through rebar, centers up & extends above finished surface. Cut a slot in your sonotube & it will slide over the conduit. Slot should be slightly more than distance from highest conduit to bottom of hole.
You have PVC running 24 inches, stubbing up in center. 4 or 5 foot depth or whatever on concrete pedestal. Dig hole deep as needed. Center stub ups, extend above surface level. Cut a slot in sonotube to slide over conduits. BE SURE PVC IS WELL GLUED, A SLIPPED COUPLING MEANS A CONDUIT PLUGGED WITH CONCRETE.
Your light should have a template, to properly center conduit(s) and set anchor bolts in right position. Use template to make a wood frame or use unistrut. Nut anchor bolts to frame and lay frame across sonotube. Tie wire frame to edges of sonotube. Be sure conduits are above surface level & well taped or capped. Coat nuts & bolts with grease or oil to keep concrete from adhering. After concrete is poured, double check frame for alignment & plumb. Also, if using square poles, be sure bolts are aligned for needed alignment of poles.
Follow all specs on size & length of anchor bolts. Use longer bolts if desired, but never shorter ones or thinner ones.
If rebar is to go into pedestal, it goes in along with stubbing up conduits, in order as needed. Last 1 I did, in 2002, we had a 6 foot deep pedestal, 5 ft in ground, 1 ft above, 4 ft diameter, with 3 or 4 rebar rings. We drove bars into ground, tied rings to uprights, put on sonotube, placed frame.