Parrallel Conductors

Status
Not open for further replies.

trip

Member
Is it allowed to parallel conductors (500kcml) in a single mast thru roof, would 392.8(D), Or something similar require two masts.
 
Re: Parrallel Conductors

Yes you can use one mast, but you have 6 conductors not 3 and have to derate for fill.
 
Re: Parrallel Conductors

If it's 3 phase 4 Wire you would have to use 5" conduit, 3 phase Delta you would have to use 4" conduit .I would install two conduits. You would also have to derate the conductors using table 310.15(2)(a). :D

[ March 22, 2005, 11:07 PM: Message edited by: highkvoltage ]
 
Status
Not open for further replies.
Top