Part-winding motor starter

Status
Not open for further replies.
QES said:
can you use a part-winding motor starter for a wye start delta run motor?
A part-winding motor starter is a new one on me.
Or maybe a different description of some kind of reduced voltage starter?
Maybe, for my benefit, you could elaborate a little?
 
QES said:
can you use a part-winding motor starter for a wye start delta run motor?

Contactors are contactors, so if you do enough rewiring the answer could be yes. Of course you would need to check the rating of each contactor.

From what I remember, a part winding starter uses (1) 4-pole and (1) 2-pole contactor. but, an open-transition wye-delta would use (2) 3-pole and (1) 2-pole contactor. I know there are other possible wiring diagrams available.
 
No, a Part Winding motor starter is specifically for a motor configured for Part Winding (PW) start. Literally, the winding is split in two, so to start it you are connecting only a portion of it, then to run you connect the rest by just adding it in; no transition. There are two contactors, one for each part, and a simple timer.

For a Wye Delta start, you need 3 contactors and a special timer and/or control circuit that changes the wiring pattern of the leads in an open transition (meaning for a moment, the contactors must be open). Plus the motor configuration and wiring is totally different.

There are however, motors with multiple leads brought out to the pecker head that can be configured in the field for either Part Winding or Wye Delta start. The starters are still completely different though.
 
For some reason part winding start is much more popular on large A/C chillers than on other motors, at least in the UK.

All the ones that I have seen have have six leads, connected to two identical 3 phase windings (connected internally in delta or Y )
This arrangement limits the starting current by first connecting one set of windings to the supply, and then after a short delay also connecting the other set.

Such motors appear vulnerable to insulation failure between the two sets of windings, rather than to earth.
 
Jraef said:
No, a Part Winding motor starter is specifically for a motor configured for Part Winding (PW) start. Literally, the winding is split in two, so to start it you are connecting only a portion of it, then to run you connect the rest by just adding it in; no transition. There are two contactors, one for each part, and a simple timer.

For a Wye Delta start, you need 3 contactors and a special timer and/or control circuit that changes the wiring pattern of the leads in an open transition (meaning for a moment, the contactors must be open). Plus the motor configuration and wiring is totally different.

There are however, motors with multiple leads brought out to the pecker head that can be configured in the field for either Part Winding or Wye Delta start. The starters are still completely different though.
Can you replace a part winding motor starter with a soft start or do you need to replace the motor?
 
Part Winding Motor with Soft Start

Part Winding Motor with Soft Start

I have a part winding motor. Is it possible to start it with a soft start instead of the part winding starter? If so, would you wire it up to the soft start in the run configuratiuon?
 
Reeves431 said:
I have a part winding motor. Is it possible to start it with a soft start instead of the part winding starter? If so, would you wire it up to the soft start in the run configuratiuon?

Huh, strange. I answered this a while ago and it didn't show up...

Yes, you can use a soft starter. Just run all 6 leads to the soft starter and connect the two windings in parallel. Make sure the soft starter is big enough, i.e. don't go by the size of the contactors because each one is only carrying a portion of the load. Use the motor nameplate FLA to size the soft starter.
 