hello there, can someone briefly describes on dual voltage motors in part winding motors? any links will help too![]()
To do a wye-delta start, you would need a 12 lead motor. I know that isn't exactly what the OP asked, but it is something worth knowing on this topic.
The key is the motor must be rated for applied voltage when connected in the delta configuration, but that is somewhat typical with North American made motors if there is six leads. I believe European motors may be more common to have a six lead motor intended to be used as a dual voltage motor connected wye for high voltage and delta for low voltage.In the link I posted it shows 3 coil/6 leads???
to start apply V PH/sqrt3 or ph-neut
then transition to delta for full V ph
starting V is 58%
running 100%
As a water/electric utility, we use part winding start motors for all of our pumps 75HP (probably 100 or so) and below. Some older motors up to 250HP are still part winding start. 25HP and smaller are across the line. All are 480V. They are simple and reliable. Wired just like the link shows. Ours are 6 or 9 wire. They are NOT Wye/Delta. On larger motors, we find that a soft start is less maintenance and allow us to use single voltage, 3 wire motors, which are cheaper. Time delay between start and run is 1-2 seconds. The part winding start reduces inrush current when starting. That makes voltage sags less noticeable on the lines feeding nearby customers. We get enough complaints as it is.....
Here's a link: http://www.usmotors.com/TechDocs/ProFacts/Typical-3ph-Connections/PWS-WYE-Dual.aspx
The first link you gave is a star/delta starter. The second link says star only for 480V but you need a special winding. Does that mean you are only using half the windings on start up?Here's another link probably more like what we use: http://www.usmotors.com/TechDocs/ProFacts/Typical-3ph-Connections/PWS-WYE-Single
The first link you gave is a star/delta starter. The second link says star only for 480V but you need a special winding. Does that mean you are only using half the windings on start up?
I don't see stuff like this often anymore
usually in older water/wastewater plants
recently saw a 2 speed 6 lead 125 HP 480 vac
used a vfd on the hi-speed configuration
controlled air Q and P with a piping bypass/control valve
I was one of those guys that lumped star/delta and part winding together. Jaref's post straightened me out.Yes...you only use half of the winding on startup, then the other half is cut in. That's why they're called "part-winding" start....
Has to be special enough to have two sets of windings and the leads to them made accessible, A motor with only three leads is not going to work with this starting method, and dual voltage 9 lead wye motors wouldn't be able to do it when connected to the higher input voltageYes...you only use half of the winding on startup, then the other half is cut in. That's why they're called "part-winding" start. No special motor that I'm aware of, but then, I wasn't the one doing the ordering, so I can't say for sure. Looking at the diagram, it looks like a standard 9 wire dual voltage motor. Wired with 3 wires from each contactor. We color code ours with tape...one set with one B,O,Y tape and one with two. If I remember right, (been a couple of years), each starter has overloads and the contacts are wired in series, so that if either one trips, the start circuit is opened.