Every design I've seen at this airport supplies (PBB's) with a 480 volt, 3-phase 4-wire w/ground service of varying sizes depending on the options provided. The problem is a secondary transformer within the service disconnect that supplies 208/120 volts for lighting, heat, limits, and drive movement. This transformer could be a 71/2 kva, 10 kva, or a 15 kva in size. There is always the appropriate sub-breakers for the transformer, lighting, heating, limits, and drive circuits but think, the secondary of the transformers derives it's neutral from the equipment grounding conductor attached to the frame of the Boarding Bridge. Doesn't that make the (EGC) a current-carrying conductor? The neutral block is bonded to the can. The service neutral is dead-ended on a isolation block and never used. As a state certified electrical inspector with 11 years experience, it never ceases to amaze me of the bull-headedness of some electrical engineers. For years now I've required every (PBB) to have a ground rod poured within the footer, cadwelded and lugged to the (PBB) pedestal running solid to the secondary transformer's neutral (XO) isolated from the primary (EGC), to ensure the lost of the primary (EGC) will not injure or kill anyone. Is that overboard? Another related problem is the transformer's temperature rating (105/150 degrees) in an unventilated disconnect cooks the insulation off the wires. I've measured 210 degrees internally to the transformer! Yet, it carrys an UL listing. Simply amazing...maybe I'm wrong.