We have a cabin in a rural area that is fed by an OH 120/240 single phase service. The service conductors enter the riser, go through the meter can, exit the meter can into an enclosure with a 200A two pole main breaker/disconnect. In this enclosure the neutral and grounding electrode conductor are bonded together. The feeder wires exit this enclosure, pass through a short conduit nipple in the exterior wall of the cabin where they then enter the main panel located inside the cabin. Simple enough.
Now then, we have a built a small shed and chicken coop separate from the cabin which we would like to install a sub-panel in.
If this cabin had 'ordinary' exterior walls I would simply drill a hole, run conduit from the main panel outside and then to the shed. Unfortunately the walls of this cabin are made of some earthen hippie mud/adobe-esque material. Maybe it's not a big deal to drill through, but I don't want to find out right now... I just want some power at the shed.
My question is this:
Is it permissible for me to install a dual pole breaker in the main panel and run the feeder wires (for the shed sub-panel) out of that breaker through the conduit where the feeder wires from the 200A main/disconnect enter the main panel? NEC states mixing feeder and service conductors in same raceway is prohibited. In this case (that I am describing/proposing) they would be, briefly, in the same enclosure as the main disconnect breaker, which is of course fed by the service conductors.
Now then, we have a built a small shed and chicken coop separate from the cabin which we would like to install a sub-panel in.
If this cabin had 'ordinary' exterior walls I would simply drill a hole, run conduit from the main panel outside and then to the shed. Unfortunately the walls of this cabin are made of some earthen hippie mud/adobe-esque material. Maybe it's not a big deal to drill through, but I don't want to find out right now... I just want some power at the shed.
My question is this:
Is it permissible for me to install a dual pole breaker in the main panel and run the feeder wires (for the shed sub-panel) out of that breaker through the conduit where the feeder wires from the 200A main/disconnect enter the main panel? NEC states mixing feeder and service conductors in same raceway is prohibited. In this case (that I am describing/proposing) they would be, briefly, in the same enclosure as the main disconnect breaker, which is of course fed by the service conductors.