- lawrenceburg kentucky
Hello guys and gals.
I have a pump station that is backed up by a 500kwatt generator. The 6 pumps are controlled by an 18 pulse Allen Bradley vfd system. Over the last year we have replaced 3 of the 18 pulse drive systems with Schneider 6 pulse vfd and a harmonic passive filter across the input of drive. Per the manufactor instructions, the passive filter is engaged 10 secs after the drive starts. When the filter engages, the voltage from the generator starts fluctuating so much that ab drives start faulting due too input phase loss and over voltage. Generator is fine without filters engaged. We installed these filters to help reduce harmonics affecting the regulator on the generator.
Why would the passive filter be affecting the generator this way?
I have a pump station that is backed up by a 500kwatt generator. The 6 pumps are controlled by an 18 pulse Allen Bradley vfd system. Over the last year we have replaced 3 of the 18 pulse drive systems with Schneider 6 pulse vfd and a harmonic passive filter across the input of drive. Per the manufactor instructions, the passive filter is engaged 10 secs after the drive starts. When the filter engages, the voltage from the generator starts fluctuating so much that ab drives start faulting due too input phase loss and over voltage. Generator is fine without filters engaged. We installed these filters to help reduce harmonics affecting the regulator on the generator.