W wnut4 Member Dec 23, 2004 #1 Can pvc conduit be used in slabs or walls where redundant grounding is required for patient care areas.
Can pvc conduit be used in slabs or walls where redundant grounding is required for patient care areas.
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Dec 23, 2004 #2 Re: Patient Care Area Grounding No. See 517.13. Don