Article 517 requires redundant grounding in patient care areas. I have no issues with this. Why did my inspector ( who is using a Mike Holt book for inspections ) not allow MC as a fixture whip. The fixtures are above 7 1/2 feet. The ground wire was attached to the fixture and to the group grounds in the j-box above the ceiling. One chief electrical inspector in one county told me that exception #2 eliminates the redundant ground for this application, i.e. the ground wire, and that the primary ground is required, i.e. using flex (under 6 ft) with listed fittings. Another chief in another county told me that was not accurate and that mc was fine. My company has done dozens of health care facilities and this is the first time this has come up. I discussed it with my inspector and told him my interpretation but he said he is just following what M.H. wrote. He said if I found out differently, he would listen. It seems odd that a piece of spiral wrapped steel has less resistance that a piece of copper wire (We still put ground wires in all our conduits anyway even though they are not required. Its a safety thing with me). Anybody have some thoughts on this? Mike, if you read this can you respond, please.