PVC conduit was installed underground to serve floor outlets in the "patient-care-area" of a dentist office.
Citing article 517.13(A)-2005 NEC: "All Branch Circuits serving patient care areas shall be provided with a ground path for fault current by installation in a metal raceway system..."
I assume that the underground raceway in this electrical design shall be in metal raceway?
Citing article 517.13(A)-2005 NEC: "All Branch Circuits serving patient care areas shall be provided with a ground path for fault current by installation in a metal raceway system..."
I assume that the underground raceway in this electrical design shall be in metal raceway?