I just received Mike's email stating that as per 250.118(11).the outer sheath of mc cable is not listed as a suitable ground fault return path for patient care areas,and cannot be used.My question is where in 250.118(11) does it say that the mc cable is not listed, or in 250.118(9)where ac cable is?
250.118 states the equipment grounding conductor shall be one or more of the following,originally making me think that mc cable would be allowed as per 250.118(11).
	
		
			
		
		
	
				
			250.118 states the equipment grounding conductor shall be one or more of the following,originally making me think that mc cable would be allowed as per 250.118(11).
 
				
 
 
		 
 
		