Yes, but it is HCF cable. Also note that 517.31(C)(3) requires mechanical protection of the wiring of the life safety and critical branches. HCF cable does not provide mechanical protection, so its use is very limited in those branches.
 
Yes, but it is HCF cable. Also note that 517.31(C)(3) requires mechanical protection of the wiring of the life safety and critical branches. HCF cable does not provide mechanical protection, so its use is very limited in those branches.

Do you have link for CHF cable? I never seen that type
 