patient care wiring methods

Status
Not open for further replies.

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Are we talking insulated ground or isolated ground? If isolated I don't believe you connect them together as it would defeat its purpose
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Dennis, isolated grounds are not allowed in Patient Care Areas. The insulated EGC is per 517.13(B)

Roger
 