JustWork
Member
- Location
- New Jersey
Hello to you all. We have an existing mobile home in an existing development no wheels on it the home has an aluminum metal skirt vented periodically around its perimeter to close the under carriage. They have constructed a wood deck and installed a patio room with aluminum construction on top of the deck which is attached to the to the mobile home which in this case considered a dwelling.? The unit is about 25 years old with a panel is maxed out. Permits have been applied for and we are abiding by all codes as with any other installation. My installation consists of a 14/2 romex snake down the wall from the panel then we took half-inch PVC and stuck it above the cross members of the subframe of the mobilehome to the attachment point of where the deck in the mobile home meet then we sleeve the 14/2 romex through it the only part of the romex that's exposed is 8 inches from the PVC to the bottom where it enters the floor under panel. The other end enters through the ledger board attached to mobile home then stapled to the first outlet location. Because this is an aluminum room everything is surface mounted with PVC taymac boxes secured with four number 8 x 0.625 self drilling sheet-metal screws to the aluminum walls. From the floor to the box which is located 18 inches up from the floor has a piece of half-inch PVC which runs from the bottom of the box to just below the underside of the sub flooring or in this case the decking. The wiring is then looped from outlet to outlet entering the PVC sleeve to each outlet which are also strapped to the aluminum walls. The home run is not arc fault protected nor GFI protected GFI protection starts at the first outlet then protects the entire room.
My questions are as follows:
1)According to article 210.12 all dwelling units are required to have arc fault protection which we all know, but since this is a patio room and not considered a sunroom does a patio room fall under the codes interpretation of similar rooms or areas? I'm thinking yes
2) Would the underside of the mobile home be considered damp locations if it is totally enclosed around its perimeter and vented? (same conditions as crawlspace) I thinking no.
3) I feel that the installation was nothing out of the ordinary, ok I didn't install connectors on the end of the conduit to clamp the wire as required.
The installation did not pass inspection under the following violation notes.
210.12 arc fault required (ok got me GFCI has been accepted usually and I just stuck with it) Now I have to wire into the panel with MC to a metal box just under the panel install a feed thru arc fault device.
334.12 a/b5 (not sure what the 5 is maybe 4 which is wet or damp locations?)
550.15 h/a (not sure what the a is maybe should have been 1?)
Comments are "feeder must in pipe under trailer entire length" (not sure what that's about. home run maybe? which is a branch circuit?)
Ok guys let me know what you think. I have been under many trailers and seen many shit installations but based upon this last install if feel that I was just tossed in that pile.
My questions are as follows:
1)According to article 210.12 all dwelling units are required to have arc fault protection which we all know, but since this is a patio room and not considered a sunroom does a patio room fall under the codes interpretation of similar rooms or areas? I'm thinking yes
2) Would the underside of the mobile home be considered damp locations if it is totally enclosed around its perimeter and vented? (same conditions as crawlspace) I thinking no.
3) I feel that the installation was nothing out of the ordinary, ok I didn't install connectors on the end of the conduit to clamp the wire as required.
The installation did not pass inspection under the following violation notes.
210.12 arc fault required (ok got me GFCI has been accepted usually and I just stuck with it) Now I have to wire into the panel with MC to a metal box just under the panel install a feed thru arc fault device.
334.12 a/b5 (not sure what the 5 is maybe 4 which is wet or damp locations?)
550.15 h/a (not sure what the a is maybe should have been 1?)
Comments are "feeder must in pipe under trailer entire length" (not sure what that's about. home run maybe? which is a branch circuit?)
Ok guys let me know what you think. I have been under many trailers and seen many shit installations but based upon this last install if feel that I was just tossed in that pile.