PC to PLC5/20 serial communications

Status
Not open for further replies.
Hi, feller's, I'm new here (to posting that is) so please be gentle with me.
So my problem is, someone stole our reports/tally computer. DH+ cards are obsolete. My question is, can I use a RS-232 D-9 serial cable to connect to the new PC, clip the other end, connect pins 2, 3 and 5 to channel A (the DH+ port) on the PLC end and insulate/isolate the rest? Or do we really need to pony up the 3 1/2 grand for a USB-to_Data Highway + adapter cable? As, like I said, it's a reports/tally computer, so data speeds are not critical.
 
I think a PLC5/20 has a 25 pin serial port labeled channel 0. you can communicate to it via that port with a standard serial RS232 port. even a USB to serial adapter usually works.

you will have to reconfigure rslinx a little, but you would have to do that to change to any other comm adapter as well.

you cannot just connect your rs232 port to the dh+ port though. different electrical characteristics among other things.

one other possibility is a 1770-kf2 adapter. it converts your PC's rs232 port to dh+. they are often available on ebay for < $200.
 
This is admittedly an expensive option ($1000+) but you could go with a1761-net-eni which will give you Internet access to your plc. I just thought I would through that out there so you were aware of them. A small caveat, they only work with the second generation plc5 which includes yours.
 