Fault bracing is the mechanical strength given to the bus bars in the distribution board and how much mechanical force they can hold up against during a major fault event. When a fault occurs,
ALL of the Available Fault Current in the entire circuit will attempt to flow into that fault. So if for example when the equipment was built in 1968, the available fault coming from the utility transformer was 25,000A, the bracing of the bus bars, and the "Interrupting Capacity" of the breakers may have been only 25,000A and it would have been fine. But if someone installed a new larger transformer, or the utility added capacity up stream so the primary fault current increased, then that transformer may now have 35,000A or 40,000A of available fault current, but your 1968 gear is only designed for 25,000A (or also possible, it has NO design listing per modern standards). If that is the case, a fault on the system may cause the bus bars to come together and "fail with extreme prejudice", aka explode.
Here's a great treatise on this from our host, Mike Holt.
https://www.youtube.com/watch?v=EfepqZMKKck